Benjamin.vial Sep 21, 2020 02:09 AM

Hello,

I have problem with two 2-wire sensors (extensometers) that's works in 4-20 mA.

I have 100 ohm high precision resistance for each sensor, works like a CURS100. But The voltage measured is too low, I think something is not fine plugged.

Looking from CURS100 manual, I seen that the "L" terminal must be connected to the "G" power out, but I didn't. I just put a jumper wire between "L" and earth pin.

I though the earth and "G" were internally connected, but maybe they don't, and I loose some current in the earth that is not measured.

Measured should be between 100 mV and 2000 mV, but I have 33 to 100 mV.

I can provide a comparative schema if my explanation is not clear.

What's the problem ?


smile Sep 22, 2020 02:10 AM

Hi, yes post the schema. Please let me know if you use SE o Diff measurements.


Benjamin.vial Sep 22, 2020 03:25 AM

Hi,

here it is :

https://drive.google.com/file/d/1t3e1vJptIO7w1Ai06b1mrdgkpergsePO/view?usp=sharing

The picture on the left is my stuff, on the right the CURS100 scheme.

On the picture, red/yellon wires are powering a 2-wire sensor and black/white are powering a second one.

Let me know if you have any question.

Thanks,

bye.


smile Sep 22, 2020 06:16 AM

Hi, in the programm logger use VoltDiff or VoltSE?

and as described in the CS diagram, the 12V return (the negative) must be connect on one of the G and not on the GND.

G and GND are not exactly the same thing, in fact CS connects the cable shield, which maybe yours doesn't have.

I advise you to put a fuse on the 12V lines or use the SW12 if  not used, always on or if are slow measurements only when needed, calculating a delay for the heating of the sensors.

If something happens along the cable, you are better protected.


Benjamin.vial Sep 22, 2020 06:35 AM

Hi,

it's VoltDiff in the prog.

Ok I'll unplug the jumper between "L" and "G" and put one between "L" and "GND" on the two sensors.

And yes, you totally right about the fuse. I'll prepar that for my next mission.

Thanks for your help, I'll post a last message if this is finally resolve.

Bye


Benjamin.vial Sep 25, 2020 04:03 AM

Hi,

Last question before go on the field, there is a particularity on my measure station.

I have 2 sensors, but not of the same model. The first can be supplied in 12Vdc (where I'll put a fuse), and the second one can only powered by 24Vdc. So I had to plug a power convertissor, 12-24Vdc.

Here is my proposition of connection diagram: https://drive.google.com/file/d/1F52aThfV0wefGMSotG30tkLNd8p3AheS/view?usp=sharing

What do you think about it ?

Thanks,

bye.


smile Sep 25, 2020 04:52 AM

Hi

something is wrong .....


The negative of the 24 V must always pass through 100 Ohm, it cannot go directly to the G of the logger or both as in the diagram.

Also is the 24V sensor 2 or 3 wires?

is the 12to24 converter isolated or  the negative of the 12V is common to the 24V?

Smile


Benjamin.vial Sep 25, 2020 05:29 AM

So where can I connect the 24V GND ? I have 2 autonomous powering battery pack, maybe I can connect the power sypply of the sensor 2 on the other battery pack than the datalogger ?

The two sensors are 2-wires.

The converter is isolated (you can find it on radiospares ref 140-8100).


smile Sep 25, 2020 08:01 AM

Hi

make these modifications:

Eliminate the direct wire between the negative of the converter and G of the logger.
Eliminate the wire between L and G
Make a new connection between L and the negative of the converter

Unfortunately, I am not familiar with links and I don't know how to attach an image. If you want to create the new scheme and create the link as the previous ones, I will be able to confirm the correctness.

Smile


Benjamin.vial Sep 25, 2020 08:34 AM

The new sheme with your modifications :

https://drive.google.com/file/d/1Hx2NzskNMJ7fTBBjtdWy3k3Ku4-sUYjZ/view?usp=sharing

Is this correct ?


smile Sep 25, 2020 08:57 AM

Ok it's correct!

Smile


Benjamin.vial Sep 25, 2020 09:03 AM

Cool ! After thinking, I agree with your modifications, it's logical.

My station is something about 2000m high and need to be reach by foot, approximatively 2h ...

I'll let you know if all became normal after modifications !

Thanks a lot,

bye


smile Sep 25, 2020 10:13 AM

So have a nice walk! :-)